We have a fire shutter that activates via the alarm going off, have had it serviced regularly with no issues previously, and has been inspected during the recent FRA. A new company has taken the servicing contract, and has sent a quote through on the basis of the service visit for "fire shutter warning panels". This has never been raised previously, and I am struggling to find any relevant sections in any fire relegations. Can anyone shed any light on this, As I am at a loss as to whether this is required for a serving hatch.

Thanks.

Posted

I assume they mean an illuminating sign and siren to warn of 'fire shutter closing' often included in modern purpose built kits, sometimes missing from older set ups or those assembled using standard shutter parts.

The requirement for warnings may be in the powered shutter standard BS EN 13241-1:2003 (I don't have a copy) plus some form of warning would be likely under The Health and Safety (Safety Signs and Signals) Regulations 1996

Just because it wasn't mentioned before doesn't mean it shouldn't have been!