Hi, I was wondering if you have a certified FD30 fire door and replace the intumescent strips with combined intumescent smoke strips (essentially upgrading the fire door to a smoke door), does this negate the certification of the door or does it simply become a certified FD30S door?

Posted

When using smoke seals care must be taken to read both the door and seal certificate.

CF218   Page 5 image.png.44f1f3092abe4f7190fa5ec11b678723.png

However, CF341

image.png.96ba46ac7f2122b93bbe5da56a515098.png

So yes they are allowed, but at least one fin must be continuous