June 12, 2025Jun 12 comment_49943 Hi, I was wondering if you have a certified FD30 fire door and replace the intumescent strips with combined intumescent smoke strips (essentially upgrading the fire door to a smoke door), does this negate the certification of the door or does it simply become a certified FD30S door? Report
June 16, 2025Jun 16 comment_50114 The point about a certificated fire door is that the label on the top edge of the door leaf enables you to find the certificate of approval at https://www.warringtonfire.com/certified-companies/check-a-certificate Read the certificate to find out the requirements for the smoke seals. In this way the door retains it's certification and becomes FD30(s). Report
June 16, 2025Jun 16 comment_50117 When using smoke seals care must be taken to read both the door and seal certificate. CF218 Page 5 However, CF341 So yes they are allowed, but at least one fin must be continuous Report