Guest Matt Posted February 27, 2025 Report Posted February 27, 2025 Is the use of a Dorgard door release/retainer in a high-rise block of flats legally prohibited, or is it merely a recommendation? If it is legally prohibited, in what regulation? Quote
Mike North Posted March 3, 2025 Report Posted March 3, 2025 Dorgarda are not illegal, however some property owners/ landlords prohibit there use Quote
AnthonyB Posted March 3, 2025 Report Posted March 3, 2025 On 27/02/2025 at 11:54, Guest Matt said: Is the use of a Dorgard door release/retainer in a high-rise block of flats legally prohibited, or is it merely a recommendation? If it is legally prohibited, in what regulation? For which doors? There are limits on the use of indirect hold open devices depending on building use & layout and which doors are to be held detailed in BS7273-4 which whilst not law would be used as a benchmark in any legal action - use outside of this would need justification as to how it still afforded suitable safety Quote
alonso Posted April 1, 2025 Report Posted April 1, 2025 Why are dorguards not suitable in some situations? Quote
AnthonyB Posted April 2, 2025 Report Posted April 2, 2025 You would need to refer to BS7273-4 but they don't have the required failsafe's of a Category A/Critical rated hold open as if there are faults on the fire alarm they won't release and are only rated to Category B/Standard actuation at best, Category C/Indirect at worst, meaning critical locations (such as doors onto stairways) would be vulnerable. Quote