Ian London Posted August 29, 2024 Report Posted August 29, 2024 Hi, I’m hoping someone can help clarify fire door regulations for us? Much of this post is providing context; the final two paragraphs are where my questions are. Our leasehold development consists of 3 x three-storey blocks (all under 11 metres high) built in 1986 — one block has 9 flats (3 on each floor), and the other two blocks (which are joined, but have separate access doors) have 6 flats each (2 flats per floor). All flats open onto communal stairwells, with one access door from outside into the blocks, with no secondary means of escape and no fire alarms in communal areas. We have a Residents Management Company and we employ a Managing Agent to carry out maintenance. We have had three surveys in the last few years with the intention of upgrading all flat entrance doors where necessary, along with communal doors, including riser cupboard doors to comply with the latest fire regs. All but one flat entrance door is the original door from 1986, and has been designated as a notional fire door. The first two surveys stated that upgrades such as reactivating painted-over intumescent strips, replacing letter boxes, hinges, concealed closers and spyholes etc would be satisfactory. We’ve recently had a third survey which states that all flat entrance doors and frames should be replaced with new. So I’m trying to find a definitive list of requirements for fire doors in blocks of flats, but the government advice is a little vague. They make a distinction between blocks over / under 11 metres, but it’s not clear what difference that actually makes and what does or doesn’t apply to us as blocks under 11 metres. E.g. on this page fire door checks are only listed as necessary for buildings over 11 metres. Buildings under that height only need to give ‘information’ to residents, which seems to imply that the annual surveys we’re paying for are not actually required. Similarly, this fact sheet states that the 2022 Regulations applies to buildings over 11 metres in height. But it also states that for buildings below 11 metres, all fire doors should be “capable of providing adequate protection”, with no detail of what that constitutes. Likewise, this LFB page also states that the 2022 regs only apply to blocks over 11 metres. I’ve looked at the Guide for small blocks, but the scope of those guidelines are for blocks with a maximum of 6 flats, so as one of our blocks has 9 flats the guide doesn’t apply to us. So, I’ve looked at the Purpose-built Blocks guidance, but it’s from 2011 and doesn’t seem to include a list of requirements for fire doors (I confess I didn’t read all 193 pages in detail though). So, can anyone point me in the direction of a definitive list of requirements for fire doors for three-storey blocks under 11 metres? I’m hoping for a simple bullet-pointed list which lays out the specifications required. Does such a thing exist? It would also be good to understand if there is a minimum acceptable specification? Is there any leeway or some degree of subjective interpretation of regulations allowed, which would explain the differing results in the surveys we’ve had? Our previous Managing Agents emailed us in January 2023 informing us that the surveying arm of their business had met with the Head of Building Control of the local council and “agreed the requirements for the upgrade of notional doors”. This sounds like the regulations are up for negotiation and are judged on a case by case basis? Unfortunately we changed Managing Agents soon afterwards so have no record of what was agreed. Thanks in advance, Ian Quote
Mike North Posted August 30, 2024 Report Posted August 30, 2024 The height is irrelevant to fire door inspections, ALL fire doors should be inspected by a competent person a minimum of every six months and maintenance carried out on all defects. Fire Safety (England) Regulations 2022: fire door guidance (accessible) - GOV.UK (www.gov.uk) As for the different interpretations of the doors, it is a lot less work for the inspector to say that the door must be changed than listing the deficiencies and the required remedials to bring the door back to compliance. Unless there is a chain of custody, the history of the door is time consuming and difficult to track down, you pays your money and you takes your choice. Quote
Neil Ashdown MAFDI Posted August 30, 2024 Report Posted August 30, 2024 Guidance can be found at https://assets.publishing.service.gov.uk/media/65e9def95b6524001af21bcc/Fire_Safety_in_Purpose_Built_Blocks_of_Flats_Guide-update.pdf The Case Studies might prove useful as might Section 54 on Compartmentation, 55 to 59 on Means of Escape and 62.12 onwards on Fire Doors. Quote
AnthonyB Posted August 30, 2024 Report Posted August 30, 2024 You shouldn't need to ask this as you should have a Fire Risk Assessment in place that has answered this for you - as the Responsible Person I'd recommend the Resident's Management Company instruct it as some agents will use the cheapest provider and you usually end up with an FRA that either misses critical areas & puts you at risk or is OTT and costs you thousands in unnecessary work. I was asked to do an FRA by an RMC after their agent said they needed to spend tens of thousands on a fire alarm and ne doors - in reality all they needed to do was change a couple of windows so they could be used as openable vents for smoke control. For example in your case your doors are most likely to only need repair if they are in essence the original '86 fire doors (notional doors as below). Quote
Ian London Posted August 31, 2024 Author Report Posted August 31, 2024 Thanks for your replies everyone. I have a few specific questions. 1. Routine checking of fire doors In the document that Mike North linked to above, item 2.3 states that "regulation 10 applies to all blocks of flats that incorporate common parts", but in 2.4 states that regulation 10's routine fire door checks (flat entrance doors every 12 months and communal doors every 3 months) "are only required in blocks of flats in which the top storey is more than 11m above ground level (typically, a building of more than four storeys)". So, as our blocks are under 11 metres, does this mean that we don't need to have routine fire door checks? 2. Self-closers When are concealed door closers compliant? Our flat entrance doors all have concealed self-closers fitted. Most of them need to be replaced as they aren't strong enough to fully close the doors anymore. Is it correct that new concealed closers are compliant when fitted as replacements to existing notional fire doors? But not compliant to be fitted to new fire doors — new doors can only have overhead self-closers? In section 6 of the same document linked to above, photo 5 shows a concealed self-closer (the same type that we currently have fitted) — this photo implies that concealed self-closers are compliant? 3. Electrical riser cupboard doors Our previous managing agent, who told us that they had met with the Head of Building Control of the local council and “agreed the requirements for the upgrade of notional doors”, commissioned the upgrade of our electrical riser cupboard doors whereby intumescent strips were fitted and the thickness of the doors were increased (see photo below). In the recent survey, these doors were failed for the following reasons: "Door has had 6mm GypRoc applied to rear face to increase thickness from 40mm to 46mm. Fixed to rear face using drywall screws. Replace door to current regulations." Who is correct? Our previous managing agent led us to believe that the upgrades they had done brought the doors up to current regulations. If this is not the case, it's frustrating as it means we are paying twice for the same thing. Thanks for your help Ian Quote
AnthonyB Posted September 4, 2024 Report Posted September 4, 2024 On 31/08/2024 at 12:07, Ian London said: Thanks for your replies everyone. I have a few specific questions. 1. Routine checking of fire doors In the document that Mike North linked to above, item 2.3 states that "regulation 10 applies to all blocks of flats that incorporate common parts", but in 2.4 states that regulation 10's routine fire door checks (flat entrance doors every 12 months and communal doors every 3 months) "are only required in blocks of flats in which the top storey is more than 11m above ground level (typically, a building of more than four storeys)". So, as our blocks are under 11 metres, does this mean that we don't need to have routine fire door checks? 2. Self-closers When are concealed door closers compliant? Our flat entrance doors all have concealed self-closers fitted. Most of them need to be replaced as they aren't strong enough to fully close the doors anymore. Is it correct that new concealed closers are compliant when fitted as replacements to existing notional fire doors? But not compliant to be fitted to new fire doors — new doors can only have overhead self-closers? In section 6 of the same document linked to above, photo 5 shows a concealed self-closer (the same type that we currently have fitted) — this photo implies that concealed self-closers are compliant? 3. Electrical riser cupboard doors Our previous managing agent, who told us that they had met with the Head of Building Control of the local council and “agreed the requirements for the upgrade of notional doors”, commissioned the upgrade of our electrical riser cupboard doors whereby intumescent strips were fitted and the thickness of the doors were increased (see photo below). In the recent survey, these doors were failed for the following reasons: "Door has had 6mm GypRoc applied to rear face to increase thickness from 40mm to 46mm. Fixed to rear face using drywall screws. Replace door to current regulations." Who is correct? Our previous managing agent led us to believe that the upgrades they had done brought the doors up to current regulations. If this is not the case, it's frustrating as it means we are paying twice for the same thing. Thanks for your help Ian 1. Routine Checking of Fire Doors. Regulation 10 of the Fire Safety (England) Regulations does not override the inspection & maintenance regime required under Article 17 of the Fire Safety Order, it just sets a mandatory minimum interval between checks for taller buildings. For smaller blocks the HM Govt guidance is: 2. Concealed single chain uncontrolled non adjustable concealed closers (often called 'Perko's' after the original manufacturer's brand name Perkomatic) have been frowned upon since the 90's and positively discouraged since the 2000's due to issues in performance and long term reliability, but (as usual as evidenced by Phase 2 of the Grenfell Report) HM Govt shied away from explicitly disallowing them on existing buildings, happy that there non compliance with EN1154 stopped them being used on newer builds - only rising butt hinges are specifically disallowed. So as long as the closer shuts the door fully flush in frame overriding any latches it is acceptable in an older building under Article 50 guidance, which means you can't be held in breach. If they are no longer effective then they will require replacement with a modern closer (often to avoid damaging the door/leaving a hole the Perko is left in place with the chain cut and an overhead closer fitted) 3. Upgraded door. The door upgrade method you have shown has been used for decades under the Fire Precautions Act and HMO Guidance and even has some test evidence behind it and will enhance the performance of the door. It's not possible to say you are guaranteed to get the full 30 minutes of a certified new door, but subject to risk assessment it's acceptable and as I've previously answered current HMG guidance will accept older and upgraded doors in smaller blocks so you would not be in breach. Unfortunately fire doors became big business after Grenfell and dozens of companies have jumped on the bandwagon with many only having staff that can do a pass/fail inspection against a new door standard rather than work holistically in conjunction with the fire risk assessor Quote
Ian London Posted September 5, 2024 Author Report Posted September 5, 2024 Thanks for your reply Anthony, really helpful. Quote
richardinnorwich Posted September 5, 2024 Report Posted September 5, 2024 Hi Ian. I'm in a very similar role to you and with very similar mid 80s built flats in similar configurations (no 3 flats to a floor though) all ours fall under the small block scenario. I share your frustrations in finding a definitive source of information, I had a very similar post to yours a while back. I have to say this forum is the best resource I've found over the last six years for good information on various fire topics and although you might not get a definitive answer on here you will get people pointing you to relevant sources of information and giving you good solid opinions based on their knowledge and experience. I find it incredibly frustrating that multiple government publications on the same topic differ and aren't crystal clear on what needs to be done. We have 'notional' flat entrance fire doors that are of a good fit and in good order, whilst according to the current regs there is no obligation for us to upgrade or replace them as they are classed as satisfactory we took what we thought was a common sense approach to improve the existing doors and upgraded as follows; - Made sure that all door edges had no more than a 4mm gap - Fitted new CE marked hinges - Fitted New intumescent letterboxes - Fitted Intumescent brush strips - Fitted intumescent hinge pads - Wrapped all locks/spyholes with intumescent sheet, backed all ironmongery with same - Max 3mm gap at bottom of door, the best solution we found was to fit a hardwood threshold, avoided issues with carpet height and hassle of drop down bars and future repairs. - Intumescent mastic seal between door frame and brickwork. -Checked overhead closers operated correctly and adjusted/replaced where necessary. Think I've listed everything. Hope it helps Quote
Neil Ashdown MAFDI Posted September 9, 2024 Report Posted September 9, 2024 (edited) Very helpful, thanks for sharing. They seem to be the most appropriate actions and avoiding the need for replacing doors unless necessary. Edited September 9, 2024 by Neil Ashdown MAFDI To add more info Quote
Ian London Posted September 9, 2024 Author Report Posted September 9, 2024 Thanks Richard, that's a huge help. Quote
Ian London Posted September 18, 2024 Author Report Posted September 18, 2024 On 30/08/2024 at 20:53, AnthonyB said: you should have a Fire Risk Assessment in place A quick question about Anthony's comment here before I go back to our Property Manager. How long is a Fire Risk Assessment valid for? e.g. should we have one done every year, the same as the fire doors should be checked? And should the person carrying it out have qualifications / certification? Quote
AnthonyB Posted September 19, 2024 Report Posted September 19, 2024 On 18/09/2024 at 19:30, Ian London said: A quick question about Anthony's comment here before I go back to our Property Manager. How long is a Fire Risk Assessment valid for? e.g. should we have one done every year, the same as the fire doors should be checked? And should the person carrying it out have qualifications / certification? A fire risk assessment must be reviewed by the responsible person regularly so as to keep it up to date - the interval is not set in legislation but usually expected to be annually - a full new assessment isn't required unless there is reason to think the existing one is invalid or there has been a significant change in the matters to which it relates including when the premises, special, technical and organisational measures, or organisation of the work undergo significant changes, extensions, or conversions. Some Responsible Persons will have their external competent provider re-assess annually, others will review themselves in house and only reassess if there are changes or 3-5 years have passed. Both can be seen to be valid approaches & I have clients that work in both of the above - some bring me in annually, others every 2-3 years. Quote
Ian London Posted September 19, 2024 Author Report Posted September 19, 2024 Thanks very much Anthony, very helpful again. Quote
Guest MartinH Posted January 4, 2025 Report Posted January 4, 2025 I came across this while searching for information on the requirements for fire doors. I haven't found my answer yet. I live in a low rise first floor flat in England built in 2006. All the flats have been fitted with FD30 doors, but an FRA identified that some of them failed because of the gaps between the door and frame. My flat entrance door failed and I was told that I had to replace it. After a long time chasing contractors, I accepted a quote from the approved contractor for a replacement FD30 door set. The managing agent has now said it has to be an FD60 door set. I challenged this as I don't believe the regulations say it should be a 60 minute fire door. They told me their surveyor said it should be an FD60 and they have said they won't approve an FD30 installation. I can't find a definitive answer for the FD30 or FD60 requirement. Quote
Neil Ashdown MAFDI Posted January 6, 2025 Report Posted January 6, 2025 https://assets.publishing.service.gov.uk/media/639ae7e98fa8f5069839c7d7/Approved_Document_B__fire_safety__volume_1_-_Dwellings__2019_edition_incorporating_2020_and_2022_amendments.pdf Appendix C Fire Door-sets. Table C1 2A on page 138 should help. Also this: https://www.gov.uk/government/publications/fire-safety-in-purpose-built-blocks-of-flats Quote
AnthonyB Posted January 6, 2025 Report Posted January 6, 2025 On 04/01/2025 at 13:12, Guest MartinH said: I came across this while searching for information on the requirements for fire doors. I haven't found my answer yet. I live in a low rise first floor flat in England built in 2006. All the flats have been fitted with FD30 doors, but an FRA identified that some of them failed because of the gaps between the door and frame. My flat entrance door failed and I was told that I had to replace it. After a long time chasing contractors, I accepted a quote from the approved contractor for a replacement FD30 door set. The managing agent has now said it has to be an FD60 door set. I challenged this as I don't believe the regulations say it should be a 60 minute fire door. They told me their surveyor said it should be an FD60 and they have said they won't approve an FD30 installation. I can't find a definitive answer for the FD30 or FD60 requirement. Unless you don't have a protected hallway approach (30 minute non self closing fire doors to internal rooms in the flat that open onto your internal hall which would also be 30 minute fire resistant, so that there are 2 x 30 minute doors between the risk room & communal areas) then there is nothing in guidance for new builds or existing legacy properties that routinely requires a 60 minute front door. Unfortunately there is a lot of misinformation & poorly skilled people in the residential fire safety sector and if every block of flats took it's freeholder to First Tier Tribunal over excessive fire door, fire alarm and emergency light issues & resulting costs they'd have little time to hear traditional FTT cases! Quote
Guest NM3 Posted January 19, 2025 Report Posted January 19, 2025 Hi, this is interesting and helpful. In our case we live in a very solid 1930s building of local ‘architectural interest’. It’s a purpose-built concrete & brick block below 11 metres. And the stairs servicing the building are broad & clutter-free, with very little combustible material present. photo However, the assessment implied the doors to individual flats (very attractive & solid oak - photo) are probably not 30mins-fire resistant. This aspect was deemed a ‘Medium Risk’. We as residents very much wish to keep these doors as they are very much part of the architectural character/heritage of our building. What might we do to retain them ? Quote
Neil Ashdown MAFDI Posted January 20, 2025 Report Posted January 20, 2025 My advice would be to: Establish that the doors are solid core and in suitable condition, record your findings. Add suitable BSEN1154 compliant self-closing devices and make sure all doors self-close completely, reliably, smoothly and without risk of causing a 'trapping injury' - of fingers etc. Add intumescent fire seals and perimeter smoke seals. Make sure the door to frame gaps are between 2mm and 4mm (within reason). Replace the existing letter plate with a fire and smoke rated item and attend to the door threshold so that it will restrict the passage of smoke in a fire. UK Government advice about fire doors can be found at https://www.gov.uk/government/publications/fire-safety-england-regulations-2022-fire-door-guidance/fire-safety-england-regulations-2022-fire-door-guidance Quote
AnthonyB Posted January 20, 2025 Report Posted January 20, 2025 As Neil says! Did the FRA pick up the common area domestic smokes that the official guidance says aren't suitable and shouldn't be there as they confuse. Quote
Guest NM3 Posted January 22, 2025 Report Posted January 22, 2025 On 20/01/2025 at 19:52, AnthonyB said: As Neil says! Did the FRA pick up the common area domestic smokes that the official guidance says aren't suitable and shouldn't be there as they confuse. On 20/01/2025 at 13:45, Neil Ashdown MAFDI said: My advice would be to: Establish that the doors are solid core and in suitable condition, record your findings. Add suitable BSEN1154 compliant self-closing devices and make sure all doors self-close completely, reliably, smoothly and without risk of causing a 'trapping injury' - of fingers etc. Add intumescent fire seals and perimeter smoke seals. Make sure the door to frame gaps are between 2mm and 4mm (within reason). Replace the existing letter plate with a fire and smoke rated item and attend to the door threshold so that it will restrict the passage of smoke in a fire. UK Government advice about fire doors can be found at https://www.gov.uk/government/publications/fire-safety-england-regulations-2022-fire-door-guidance/fire-safety-england-regulations-2022-fire-door-guidance Hi Anthony No, they didn’t. Also consistently referred to them as Fire Alarms - So a bit confusing for us … Hi Neil We believe it might be sufficient to simply inform leaseholders of the findings & advice, as you’ve mentioned. And it will be for those individuals to decide whether to act on them. Also, as the doors are solid oak, and of 44+mm thick(pic) they could be regarded as sufficient for the 30mins. Apparently the minimum expected for purpose-built fire doors. And we could retain the period ‘30s letter plates by lining the interiors with intumescent material which would expand & seal in the event of extreme heat. Quote
Hayfever Posted February 2, 2025 Report Posted February 2, 2025 On 30/08/2024 at 10:06, Mike North said: The height is irrelevant to fire door inspections, ALL fire doors should be inspected by a competent person a minimum of every six months and maintenance carried out on all defects. Fire Safety (England) Regulations 2022: fire door guidance (accessible) - GOV.UK (www.gov.uk) As for the different interpretations of the doors, it is a lot less work for the inspector to say that the door must be changed than listing the deficiencies and the required remedials to bring the door back to compliance. Unless there is a chain of custody, the history of the door is time consuming and difficult to track down, you pays your money and you takes your choice. I am confused by this as the Regs guidance states; routine checks of fire doors that the Responsible Person must ensure are carried out - these checks are only required in blocks of flats in which the top storey is more than 11m above ground level (typically, a building of more than four storeys) So I am reading this that the 6 monthly fire door checks are not required in a premises under 11m ????? Have I missed something???? Quote
Mike North Posted February 3, 2025 Report Posted February 3, 2025 BS 9999 Maintanence I.6.1 General In addition to the checks recommended in I.2, I.3, I.4 and I.5, the checks described in I.6.2 and I.6.3 should be undertaken once every six months. Arrangements should be made for six-monthly inspections and tests to be carried out by competent persons on the fire detection and fire alarm systems, the sprinkler systems, any extinguishing systems, the emergency and escape lighting systems and the firefighters lift, for any defects found to be logged and the necessary action taken, and for certificates of testing to be obtained. I.6.2 Fire doors All fire doors should be inspected every six months. In particular, it should be ensured that: a) heat-activated seals and smoke seals are undamaged; b) door leaves are not structurally damaged or excessively bowed or deformed; c) gaps between the door leaf and the frame are not so small as to be likely to bind, or so large as to prevent effective fire and smoke-sealing; d) hanging devices, securing devices, self-closing devices and automatic release mechanisms are operating correctly. Quote
Neil Ashdown MAFDI Posted February 3, 2025 Report Posted February 3, 2025 This refers to the checks to satisfy Regulation 10 of the Fire Safety (England) Regulations 2022 https://www.legislation.gov.uk/uksi/2022/547/regulation/10/made But if your property is not in-scope there is still a requirement to ensure your fire doors are suitable and in good condition, refer to Article 17 of the Fire Safety Order https://www.legislation.gov.uk/uksi/2005/1541/article/17 Quote
AnthonyB Posted February 3, 2025 Report Posted February 3, 2025 22 hours ago, Hayfever said: I am confused by this as the Regs guidance states; routine checks of fire doors that the Responsible Person must ensure are carried out - these checks are only required in blocks of flats in which the top storey is more than 11m above ground level (typically, a building of more than four storeys) So I am reading this that the 6 monthly fire door checks are not required in a premises under 11m ????? Have I missed something???? Falling into the trap of reading legislation in isolation. Even before the Fire Safety (England) Regulations there was a legal requirement under Article 17 for ALL premises subject to the Fire Safety Order to have a suitable system of maintenance for fire safety measures (including fire doors) however it didn't set intervals leaving that down to guidance & risk assessment. Due to there being a general failure in those managing flats to comply with this the Government introduced prescriptive requirements for the intervals that must be followed for blocks over 11m, but did not remove the existing requirements for other blocks, where guidance suggests 6 monthly communal door checks and annual flat front door checks (but not to 'best endeavours' like larger blocks.) Quote
Guest Guest Posted July 31, 2025 Report Posted July 31, 2025 We live in a block of flats that is below 11 meters, has a ground floor, first floor and a top floor. Each floor has 2 apartments - front doors facing each other. There is a main communal entrance to the block of flats. I've found the information above useful. However, one question I have, which i'm unable to find a definitive answer to, is that, if the building is below 11 meters and only two apartments per floor, both with FD30s front doors, is there STILL a requirement for communal double doors on the ground and first floor? These communal double doors are just before the entrance to both the flats on each of these floors. These doors ARE NOT the communal front door that faces outside. The estate was constructed in the early 1980s. The doors are very impractical and open inwards and make it really difficult for those living in the flats to navigate furniture, pushchairs, etc in and out of their property. Also, if the flat owners have FD30s Fire Doors installed as their front doors, is there a requirement for another set of communal double doors between their apartment and the hallway? Fire Assessors have said that the communal double doors need in-tumescent strips and the right hinges, but no one has definitively said, or pointed to legislation that confirms these doors are actually required. If anything, in their current form, they pose a big safety risk. Would welcome any advice. Quote