July 12, 20233 yr comment_37431 With the legal requirement of an FRA being life safety over property protection, does this include the risk to fire fighters too? For example, when assessing compartmentation of a premises, it may not be deemed necessary for the protection of people on site. However, it could result in a small fire becoming a much bigger fire, therefore putting fire fighters at risk. Does this need to be considered, as it will of course involve an extra cost. An an example, the door of a boiler cupboard in a historic building. No impact on escape routes, etc, but obviously a high fire hazard. Would a fire door be needed? Thanks! Report
August 1, 20232 yr comment_37801 I understand your point, but it if the premises is largely compliant in terms of life safety anything you recommend would have to be backed up by a strong argument. Especially if there is a significant cost attached. If you consider large insulated sandwich panel buildings, they are not designed for firefighter safety, at all! Report
August 1, 20232 yr comment_37810 On 12/07/2023 at 16:03, AdamR said: With the legal requirement of an FRA being life safety over property protection, does this include the risk to fire fighters too? For example, when assessing compartmentation of a premises, it may not be deemed necessary for the protection of people on site. However, it could result in a small fire becoming a much bigger fire, therefore putting fire fighters at risk. Does this need to be considered, as it will of course involve an extra cost. An an example, the door of a boiler cupboard in a historic building. No impact on escape routes, etc, but obviously a high fire hazard. Would a fire door be needed? Thanks! The legislation as written does not consider fire fighters in the course of operational fire fighting duties to be relevant persons so in essence - no! Report