Jump to content

Mr


Guest Guest

Recommended Posts

I have just inspected a fire door and the lock is the wrong size it is 250 x 20 its  longer than the specified 150 x 20  stated in the test certificate.Should the door be replaced with the correct size lock ?

Link to comment
Share on other sites

1) Contact the door leaf manufacturer for advice.

2) How critical is the fire door to life safety? Would replacement provide an improvement commensurate with risk?

3) Are there alternatives to replacement in mitigating the risks around the non-compliance issue? (given that the door will need to be repaired to accept a smaller lock)

Link to comment
Share on other sites

Join the conversation

You are posting as a guest. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

Loading...
×
×
  • Create New...