  1. There is no legal requirement to have the CF number on the top of the door, it merely proves that the door blank manufacturer was a member of the scheme at the time of manufacture.  It does however make it easier to prove the door is a fire door, the invoice should provide this information.

    The brush seal is there for cold smoke and not fire

  2. Smoke seals are designed to contact the closed door edge, that what they will stop the passage of smoke.  They should not overly hinder the door from closing, however if the seals are too tight then they can cause an over-pressure delaying or even stopping the door from closing

  3. In most cases on a 30 min door pads are not required, however you must refer back to the door assessment (which obviously you can’t).  For a FD30 hardwood door, personally I would forget the intumescent pads.

     

    Should I fit intumescent pads behind my fire door hinges? - Armada (armadadh.com)

     

    In many cases (but not all), the fire test assessment for the door states that for standard sized FD30 doors, intumescent hinge pads are not required.

    For instance the BM Trada Field of Application Report for the Strebord 44mm FD30 door core states that hinge pads are not required for doors of height 2670mm and under. Doors of height 2671mm and over need 1mm intumescent pads under both hinge leaves.

    Likewise, BM Trada’s Field of Application Report for the Halspan Optima 30 door core, simply says; hinge intumescent protection not required.

    And a third example is Jeld-Wen’s Tubeboard FD30 door core, where the Certifire Certificate of Approval also says; none required.

  4. Andy,

    This is probably a dictat from the NHS, I have the same from the DIO.

    In some cases, it does make sense.

    1.       The door guard must be positioned so that the alarm is loud enough to close the door.

    2.       You need a management control to close the doors over night to stop the doors twisting over time.

    Also para C6 approved doc B

    C6   If a self-closing device would be considered to interfere with the normal approved use of the  building, self-closing fire doors may be held open by one of the following.

    a.    A fusible link, but not if the doorset is in an opening provided as a means of escape unless it complies with paragraph C7.

    b.    An automatic release mechanism activated by an automatic fire detection and alarm system.

    c.    A door closer delay device.

     

  5. Intumescent pads have never been a requirement for FD20 doors (unless there is a specific requirement in the manufactures instructions).  The current regulations only require a FD20 door (not smoke) for an enclosure of a stairwell for a single-family dwelling you could argue the point with the surveyor. It is common practice and has been for some considerable time to use 1 and ½ hinged on all heavy door sets (not just fire doors) so you may wish to add a hinge. 

  6. What you have to consider any small items like smoke seals and minor adjustments.  Will these be included in the cost of inspection, or will they be a separate visit by the maintainer?

    Once the doors are up to spec, are you going to use the same company for on going maintenance.  There is the benefit that the maintainer can not say in subsequent rounds that the door is now noncompliant or needs lipping if they didn’t say that in the initial inspection.