  1. Horizontal positioning affects the ability of the device to self-close the door. Check with Geofire before installing in a fixing position that differs from the installation instructions.
  2. Neil Ashdown CertFDI

    Adding vision panel to fire door

    I would recommend seeking the advice of a certificated fire door inspector at www.fdis.co.uk/inspector Vision panels may be retro fitted in some fire doors provided the work is done correctly and the door is suitable so you need advice from somebody qualified to carry out the necessary inspection work.
  3. Neil Ashdown CertFDI

    Simple magnetic door catches

    I would recommend seeking advice from your local certificated fire door inspector at www.fdis.co.uk/inspector A competent fire door inspector can survey the doors and advise on a suitable door hold open device.
  4. Neil Ashdown CertFDI

    Boiler room fire door - is a door closer required?

    Hi Tom, Current UK building regulations require that fire resisting doors either have a self-closing device (Fire Door Keep Shut) or a suitable lock (Fire Door Keep Locked). Most fire resisting doors are also required to restrict the spread of cold smoke and therefore cold smoke seals are fitted to the top edge and vertical edges of the door leaf or to the door frame. The threshold gap is limited to 3mm for the same reason. It is likely that cold smoke protection would be a requirement at residential premises especially if the door is located on an escape corridor or staircase. This being the case a smoke damper would be preferable to an air transfer grille so as to restrict spread of cold smoke in a fire.
  5. You must check that the door leaf is suitable before attempting any upgrading works. Contact your local certificated fire door inspector for advice at www.fdis.co.uk/inspector
  6. Neil Ashdown CertFDI

    Plug in fire door?

    You should ensure that: a) The door leaf self closes (from any angle) all the way onto the rebate stop of the door frame, overcoming resistance from seals and latch bolts. Procure a suitable self-closing device to minimum power-size 3 BS EN 1154. b) The smoke seals must fill the gap between the door leaf and door frame. c) The gap at the threshold should be no more than 3mm. Otherwise gaps up to 10mm require sealing with a threshold seal. The above is a guide and is not exhaustive. If in doubt refer to your local fire door inspector at www.fdis.co.uk/inspector
  7. Neil Ashdown CertFDI

    Why do I need a door closer?

    Hi Mary B, There is indeed a requirement to take measures to restrict the amount of smoke that can pass under or around a fire door. Failure to do so is a breach of the Regulatory Reform (Fire Safety) Order 2005. If the fire door leaf has been trimmed at its bottom edge so that the gap between the bottom of the door leaf and the threshold is more than 3mm then the threshold strip on the floor will have to be increased in height accordingly. Alternatively a maximum gap of 10mm is allowed but a smoke seal must be fitted to the bottom of the door leaf to fill the gap. The fire door should also, of course, have effective cold-smoke seals to seal the gap between the door leaf and the door frame at the top edge and both vertical edges. Guidance is available in BS 9991 Fire safety in the design, management and use of residential buildings Code of practice and BS8214 Timber-based fire door assemblies. Code of practice. Also more information can be found at www.ifsa.org.uk You should inform the House Manager without delay.
  8. The correct door edge to door frame gap depends on the fire performance test evidence for that particular fire door. So the gap could be more than 4mm for some fire doors and still be compliant with the fire performance test. However for most timber-based fire doors the gap should be between 2mm and 4mm. If gaps are too large it may affect the door's fire performance and importantly would allow cold smoke to spread past the brush/blade edge seal and thus compromise safe escape. Therefore action should be taken to correct gap issues and cold smoke restriction issues as obligated by Article 17 of the Regulatory Reform (Fire Safety) Order 2005 for England & Wales. Many people are killed by the effects of smoke spread rather than the fire itself.
  9. Neil Ashdown CertFDI

    Entrance door

    The reason entrance doors to individual flats are required to be fire resisting and cold smoke restricting is to protect the common area (outside the door) from the effects of fire and smoke. This is so that other people can use that part of the common area to escape safely. You say that your door opens onto a path. Is the path outside in the open or inside part of the building and who would benefit by being able to use the area outside your flat entrance door in the event of a fire? By providing this information to your management company they should be able to tell you if the door needs to be a fire resisting door, and if so why.
  10. Neil Ashdown CertFDI

    cutting the door stop to fit a maglock on FD30

    You should be aware that, in a fire situation, heat transfer from this large amount of metal to the timber door leaf could cause premature fire separation failure. The top edge and the upper part of the closing edge is more vulnerable to fire (than the lower parts of the door leaf) and therefore it would be sensible to risk assess the effects of a premature failure for the timber based doors that are fitted with magnetic locks. With regard to removal of stops, it is always better to add a timber fillet to the door frame reveal instead so as to support the hardware securely. I realise this may not be very practical, but fitting such a device to the door-frame closing jamb doesn't seem very practical anyway! You should also bear in mind that mag-locks tend to distort the timber door leaf where they pull the leaf towards to magnet. During installation, care should be taken to ensure the leaf remains in plane in its closed position.
  11. Neil Ashdown CertFDI

    Fire door glazing upgrade

    Aside from the important issue of checking that the doors are suitable as FD30s doors you can find information in the Glass & Glazing Federation 'Fire Resistant Glazing Best Practice Guide' at http://www.ggf.org.uk/groups/fire-resistant-glazing-group/fire_resistant_glazing_best_practice_guide Also check out latest guidance from the Ministry of Housing, Communities & Local Government at https://assets.publishing.service.gov.uk/government/uploads/system/uploads/attachment_data/file/707440/Advice_for_building_owners_on_assurance_and_replacing_of_flat_entrance_fire_doors.pdf and from the National Fire Chiefs Council at https://www.nationalfirechiefs.org.uk/High--Rise-Safety-for-Residents
  12. Neil Ashdown CertFDI

    Boiler room fire door - is a door closer required?

    Will the intumescent air transfer grille restrict the spread of cold smoke?
  13. Neil Ashdown CertFDI

    Why do I need a door closer?

    Hi timbo, To achieve compliance the self-closer you install must be to minimum power-size 3 to BS EN 1154. Select a self-closer that has power adjustment up to size 4 or 5 with adjustment for both closing speed from fully open to almost closed as well separate adjustment for the latching action. This type of self-closer, correctly adjusted, will close the door correctly overcoming any latch bolt resistance and close quickly enough to satisfy your requirements.
  14. Neil Ashdown CertFDI

    Is my door a fire door?

    Hi Silvia, Find your nearest Certificated Fire Door Inspector at www.fdis.co.uk/inspector They will be able to help.
  15. Hi MHO, You don't say if the building has had any work done regarding the fire doors that would be subject to current building regulations. So assuming the answer is no and the fire doors were installed 18 years ago when the building was built, the question is: Do you need to upgrade to three hinges per fire door? A fire door inspector should check several points (depending on the fire door rating) regarding the hinges: a) That they are suitable for the fire door and in good serviceable condition, b) That all correct size fixing screws are present and that the hinges are securely fixed to the door and frame and c) That there are three or more hinges fitted at the correct positions either because its a requirement to comply with the evidence of performance for the fire door or to comply with BS 8214 the Code of Practice for Timber Based Fire Doors. Timber based fire doors (unless very small cupboard doors) should have three or more hinges to meet the required fire separation performance by helping to prevent or limit distortion of the door at mid-height in a fire situation. The fire performance of the door can only be as good as the hinge fixings used to secure it to its door frame. So if there are three hinges rather than two then the fire performance will that much better! Fire doors are covered by the Regulatory Reform (Fire Safety) Order 2005 and Article 17 of the Order requires that Fire Doors...... are subject to a suitable system of maintenance and are maintained in an efficient state, in efficient working order and in good repair. http://www.legislation.gov.uk/uksi/2005/1541/article/17/made
×