  1. Hi Tom

    Yes, both the Rollo and the Easyscape fire escape ladders would do the trick. The problem is that our manufacturers do not have insurance cover for sale to the USA and Canada (the old story about high liability claims in the USA and Canada). So we can send these fire escape ladders anywhere in the world but North America. I am really sorry about this. It really shows that lawyers do not only affect large corporations but also consumers.

    Harry

  2. Hi Tom

    Sounds like you really could do with interlinked smoke alarms, considering that you might not hear an alarm being set off in the kitchen at night. I would suggest battery operated radio-interlinked smoke alarms in your case.

    Kitchen: heat alarm

    hallway, bedrooms, living rooms: optical smoke alarm

    landing: ionisation smoke alarm

    The self-adhesive stickers work a treat but you have to remember that you need to take the alarm off after 10 years, so some painting might be needed then.

    There is a radio-interlinked smoke alarm family available with Strobe/vibration pad units

    One thing intrigues me, you mention a loft conversion. Normally, when converting lofts you will have to install interlinked smoke alarms in the now converted loft and along the escape route. That does not seem to have happened.

    Harry

  3. Hi Ted

    HMO

    House in multiple occupation, as defined in section 254 of the Housing Act 2004

    Meaning of “house in multiple occupation” (please check at legilation.gov.uk for the latest version)

    (1) For the purposes of this Act a building or a part of a building is a “house in multiple occupation” if—

    (a) it meets the conditions in subsection (2) (“the standard test”);

    (b ) it meets the conditions in subsection (3) (“the self-contained flat test”);

    (c ) it meets the conditions in subsection (4) (“the converted building test”);

    (d) an HMO declaration is in force in respect of it under section 255; or

    (e) it is a converted block of flats to which section 257 applies.

    (2) A building or a part of a building meets the standard test if—

    (a) it consists of one or more units of living accommodation not consisting of a self-contained flat or flats;

    (b ) the living accommodation is occupied by persons who do not form a single household (see section

    258);

    (c ) the living accommodation is occupied by those persons as their only or main residence or they are to

    be treated as so occupying it (see section 259);

    (d) their occupation of the living accommodation constitutes the only use of that accommodation;

    (e) rents are payable or other consideration is to be provided in respect of at least one of those persons'

    occupation of the living accommodation; and

    (f) two or more of the households who occupy the living accommodation share one or more basic

    amenities or the living accommodation is lacking in one or more basic amenities.

    (3) A part of a building meets the self-contained flat test if—

    (a) it consists of a self-contained flat; and

    ( b ) paragraphs ( b ) to (f) of subsection (2) apply (reading references to the living accommodation

    concerned as references to the flat).

    (4) A building or a part of a building meets the converted building test if—

    (a) it is a converted building;

    ( b ) it contains one or more units of living accommodation that do not consist of a self-contained flat or

    flats

    (whether or not it also contains any such flat or flats);

    (c ) the living accommodation is occupied by persons who do not form a single household (see section 258);

    (d) the living accommodation is occupied by those persons as their only or main residence or they are to be

    treated as so occupying it (see section 259);

    (e) their occupation of the living accommodation constitutes the only use of that accommodation; and

    (f) rents are payable or other consideration is to be provided in respect of at least one of those persons'

    occupation of the living accommodation.

    (5) But for any purposes of this Act (other than those of Part 1) a building or part of a building within

    subsection (1) is not a house in multiple occupation if it is listed in Schedule 14.

    (6) The appropriate national authority may by regulations—

    (a) make such amendments of this section and sections 255 to 259 as the authority considers appropriate

    with a view to securing that any building or part of a building of a description specified in the regulations

    is or is not to be a house in multiple occupation for any specified purposes of this Act;

    ( b ) provide for such amendments to have effect also for the purposes of definitions in other enactments

    that operate by reference to this Act;

    (c ) make such consequential amendments of any provision of this Act, or any other enactment, as the

    authority considers appropriate.

  4. Hi Gertrud

    The amber light indicates that the rechargeable backup battery of the radio-base (Ei168) is running low or not re-charging properly.

    First thing to check is that the internal 'Battery on' switch is properly triggered. Remove the smoke alarm with the help of a screw driver and press the 'on' switch on the base plate. (see picture of switch in manual)

    If that does not resolve the issue, check that the power supply is not switched. This can happen if the wiring coming from the nearest light fitting to the alarm has been installed incorrectly. Switch the light, from which the smoke alarm is fed with power, on and leave it on for 24 hours; if the amber light stops, call out the elctrician to check wiring. If the amber light continues, it could be a battery damage. In this case contact your retailer.

    Harry

  5. Hi

    Dorgards are programmed to release every 7 days to avoid warping. In addition you might want to consider setting them for night time release. In that case they will close every night. This also helps to prevent any warping of the fire door.

    If you have fire door prone to warping you might want to consider a free swing door closer that doe not apply any force on the door during normal operation.

    Harry

  6. Hi Tom

    Just checked with our manufacturer who supplies our CO2 refurbs. Their answer was:

    It is not possible to Kitemark a refurbished CO2 extinguishers as BSI will not permit the use of their mark for refurbs. This is linked to the fact that they cannot certify the origin of the cylinder (issue of traceability). However, BAFE is approving the refurbs we are selling and there is a 21 step process involved to stress test and pressure test the cylinders to ensure the integrity of the cylinder. The cylinders are also sand-blasted, re-painted and labeled and then fitted with brand new head valve assemblies.

    Whilst they can be used in new installations, they are mainly used to replace existing CO2 extinguishers when an extinguisher reaches 10 years.

    Harry

  7. Hi

    Our supplier of emergency lights, Ringtail, recommends that lamps in maintained bulkheads are changed every six months. The longevity of emergency lights is better if lamps are changed before they are fully failing. However, this recomendation probably only applies if your organisation has a contractor for the maintenance of your emergency lighting and the costs of a call-out were to be substantial. In such a case pre-emptive maintenance (changing while the light is still working) makes sense.

    Harry

  8. Hi

    Usually you would choose from a range of sizes when purchasing a new fire door.

    Typical glazed window sizes (in mm) are

    457 x 457

    150 x 1410

    229 x 914

    two panes (top 150 x 760 and bottom 150 x 450) to ensure wheelchair users can see through the glazing.

    As I say these would normally be ordered at the time of fire door purchase (see http://www.safelincs.co.uk/Fire-Doors-with-30-minutes-protection-FD30/ as an example)

    If you consider retro-fitting fire door glazing you must use an approved installer.

    Harry

  9. Hi Pam

    Tom is entirely right about stating that you can lock fire doors over night etc if premises are empty at this point. However, there always remains the residual risk of forgetting to open up a fire door which is also a fire exit at the start of business (of course only if the fire door is not the main entry point of the building). You could have a panic bar or panic latch on the inside of the fire door and something like a keypad on the outside to achieve secure and safe fire exits.

  10. Hi Chris

    I am assuming we are talking here about mains powered emergency lights with backup battery. The regular maintenance tests should identify battery failures. Eg if the emergency light does fail the annual 3 hour test, it would be time to replace the battery.

    In general it can be stated that emergency lighting batteries are required to last 4 years.

    As EN60598 2 - 22 states:

    'Self Contained Luminaires shall incorporate batteries which are designed for at least 4 years of normal operation. These batteries should only be used for emergency related functions within the luminaire or its satellite.'

    That does not mean that you have to replace before then or after.

  11. Hi Ryan

    the systems I have seen approved for otherwise classical part 1 situations were categorized BS5839 part 6 grade D (mostly radio-interlinked), although they had call points and sometimes control switches for silencing and identification which takes them closer to panelled systems. These can be well suited for small business premises of low risk. The size of the building is important in this consideration, as one part of the role of a central control panel is to provide directions to fire fighters, which of course is pointless in small office buildings. The other advantages of panels of course are system monitoring and call facilities.

    Harry

  12. Hi Ryan

    I agree with you for larger businesses and obviously in this case we do not know how big exactly the premises are etc. However, I think that it is important to point out that it is ultimately the decision of the business and its responsible person how to cover the fire risks identified in their Fire Risk Assessment. Many small to medium businesses have installed BS5839 part 6 systems with full approval of their local fire brigades etc. British Standards are mostly recommendations and whilst they reflect best practice, business owners do not have to follow them unless there is additional governmental guidance or insurance requirements stating so. For small businesses without special risks, where the fire brigade does not benefit from pin-pointing the source of a fire, a panelled system is a bit of an overkill in my eyes.

    Harry

  13. I would say that from a practical point of view, a normal caretaker would be able to use a test key to remove power from emergency lights and ensure that the emergency lights stay on the required period. When it comes to repair of failing emergency lights then I guess an electrician would be needed unless the caretaker has sufficient qualifications to replace batteries and lamps.

    It is important, though, that all tests are recorded and the fire safety log book.

    Harry

  14. Hi Ken

    to 1.11: You do not have to choose any of the proposed corrective actions. You can either devise your own fire safety measure or you can explain in the text section at the end of chapter 1 why you think that no further action is needed.

    to 2.3: If you cannot get hold of a manual for your kitchen units and you have different people working in the kitchen, you should write a short instruction yourself. Explain the 'oddities' of your equipment and point out the fire safety risks (eg leaving towels on the cooker or leaving towels unsupervised on the handle of the oven)

    to 2.13 The vacuum is only in use under supervision and for short periods, so there is little risk of a fire as a result of overheating of a cable reel. However, make sure that there is no permanent load on any cable reels.

    I hope this helps

    Harry

  15. Hi Tom

    Their main concern was that the CO patches did not have an audible alarm. So, if the patch detects any dangerous concentration of CO the people in the building would still be exposed to carbon monoxide, as they are very unlikely to check the colour of the patch turning from brown to black at that moment. Many deaths occur when people are sleeping or dozing, so there is no way these patches could help to prevent those deaths in these situations. The patches also only lasted 6 months, so that people seeing a discolourisation would be unsure if this was due to CO or age. What did not help either was the fact that in a test none of the patches detected concentrations of 50ppm and even at 350ppm not every model changed colour!

    Harry

×
×