Jump to content

HMO Fire alarm Zone plans


Guest brad

Recommended Posts

We have recently completed the maintenance of a HMO property with Grade A system, and have noticed they have no fire alarm zone plan. This is a two storey building. does the standards state they need a zone plan? as I cannot  seem to find this anywhere.

Link to comment
Share on other sites

BS5839-6 states:

"17.3 Additional recommendations for control and indicating equipment for Grade A systems
The following recommendations should be met.
a) CIE for Grade A systems should meet the recommendations given in BS 5839‑1:2017, Clause 23...."

 

BS 5839‑1:2017, Clause 23 states:

"23.2.2 The following recommendations apply to the facilities provided for visual indication
of fire signals.

...e) On or adjacent to indicating equipment, there should be a diagrammatic representation of the building, showing at least the building entrances, the main circulation areas and the division into zones. The diagrammatic representation may comprise any of the following:
1) an illuminated mimic diagram;
2) a VDU with an appropriate back up; or
3) a printed, correctly orientated, zone plan (see 3.68)."

 

So yes, they should have one.

Link to comment
Share on other sites

Join the conversation

You are posting as a guest. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

Loading...
×
×
  • Create New...