Guest brad Posted November 17, 2021 Report Share Posted November 17, 2021 We have recently completed the maintenance of a HMO property with Grade A system, and have noticed they have no fire alarm zone plan. This is a two storey building. does the standards state they need a zone plan? as I cannot seem to find this anywhere. Quote Link to comment Share on other sites More sharing options...
AnthonyB Posted November 18, 2021 Report Share Posted November 18, 2021 BS5839-6 states: "17.3 Additional recommendations for control and indicating equipment for Grade A systems The following recommendations should be met. a) CIE for Grade A systems should meet the recommendations given in BS 5839‑1:2017, Clause 23...." BS 5839‑1:2017, Clause 23 states: "23.2.2 The following recommendations apply to the facilities provided for visual indication of fire signals. ...e) On or adjacent to indicating equipment, there should be a diagrammatic representation of the building, showing at least the building entrances, the main circulation areas and the division into zones. The diagrammatic representation may comprise any of the following: 1) an illuminated mimic diagram; 2) a VDU with an appropriate back up; or 3) a printed, correctly orientated, zone plan (see 3.68)." So yes, they should have one. Quote Link to comment Share on other sites More sharing options...