AlwaysLearning Posted May 29, 2021 Report Share Posted May 29, 2021 I came across Grade D detection in the communal areas of a purpose built block of flats, it was not interlinked to the flats, would this be described as a part 1 or a part 6 system as it was communal areas? Quote Link to comment Share on other sites More sharing options...
AnthonyB Posted June 2, 2021 Report Share Posted June 2, 2021 It's a part 6 system that serves no purpose other to draw people into a smoke filled stair, usually these are either withdrawn or replaced with a compliant full evacuate system (i.e. sounders and detectors in flat lobbies) depending on the results of the FRA. You can't build a compliant Part 1 system using Grade D equipment so it can't be categorised as such. Quote Link to comment Share on other sites More sharing options...
AlwaysLearning Posted June 3, 2021 Author Report Share Posted June 3, 2021 Thankyou Anthony. Quote Link to comment Share on other sites More sharing options...