March 28, 20215 yr comment_19666 When installing a new Fire Alarm system to BS5839-1, what is the maximum distance allowed between the exit door and the MCP? I have looked at BS5839-1 but cannot find anywhere that states a specific distance (only heights from floor)? Report
March 28, 20215 yr comment_19674 The assumption is they are adjacent, so no need for a distance, what's the exact scenario? Report
March 29, 20215 yr Author comment_19678 18 hours ago, AnthonyB said: The assumption is they are adjacent, so no need for a distance, what's the exact scenario? Well...the MCP in question is approx. 4-5m distance from the emergency exit door....the occupants would have to veer away from the escape route / exit slightly to reach it (thats if they remember its there). My thinking was that it should roughly be arms length (I know everyone's arms are different length so was using 1.5m max distance as a guide) so they could hit it as they escaped? Report
April 1, 20215 yr comment_19699 That's rather stretching "adjacent"! A useful benchmark would be to take the distances from the requirement for the green manual release call points for exit doors which are also meant to be in close proximity of the relevant door - in BS7273-4 it says ".....They should be sited within approximately 2 m of the associated door(s)....." Report
April 5, 20215 yr Author comment_19720 On 01/04/2021 at 19:55, AnthonyB said: That's rather stretching "adjacent"! A useful benchmark would be to take the distances from the requirement for the green manual release call points for exit doors which are also meant to be in close proximity of the relevant door - in BS7273-4 it says ".....They should be sited within approximately 2 m of the associated door(s)....." Hi AnthonyB - yes, that sounds a lot more "adjacent" than the 4-5m! ? thanks again for your help. Report
Join the conversation
You are posting as a guest. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.