Meady Posted October 11, 2020 Report Share Posted October 11, 2020 Does anyone know if self-testing emergency escape lighting still needs a 3-hour discharge test each year?? We're looking at BS5266-1 and BS EN 50172 and we cant see where it mentions self-testing systems? Any help / guidance much appreciated. Quote Link to comment Share on other sites More sharing options...
AnthonyB Posted October 12, 2020 Report Share Posted October 12, 2020 Yes, but they do that automatically and report if they fail (either to the control panel if an integrated network or via the coded LEDs on the fitting if self contained). Just inspect them visually (& the control panel where fitted) monthly and act on the faults indicated (if any) Quote Link to comment Share on other sites More sharing options...
Meady Posted October 19, 2020 Author Report Share Posted October 19, 2020 On 12/10/2020 at 20:30, AnthonyB said: Yes, but they do that automatically and report if they fail (either to the control panel if an integrated network or via the coded LEDs on the fitting if self contained). Just inspect them visually (& the control panel where fitted) monthly and act on the faults indicated (if any) Thank you as always AnthonyB - much appreciated. Quote Link to comment Share on other sites More sharing options...
Recommended Posts
Join the conversation
You are posting as a guest. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.