Jump to content

Fire Strategy Plan for a Hotel Building


Guest Julian Wahnon

Recommended Posts

Guest Julian Wahnon

Hi!  
 
Which guidance/ documentation would be best for a fire strategy plan for a hotel building? 

Is approved doc B Vol 1/2 appropriate?
 
Many thanks in advance.  
 
Julian

Link to comment
Share on other sites

Is this hotel built yet? If not then the designer can choose between Approved Document B, BS9999 or a bespoke engineered solution following BS7974 principles.

If already running then the built fire strategy will need reverse engineering based on an examination of the construction, dimensions, active and passive fire precautions, management, etc.

Of course the term fire strategy is sometimes used for the emergency evacuation & response plan for fire in a premises or the fire safety policy document.

Guidance on existing premises is given in the DCLG Sleeping Premises guide.