July 15, 20178 yr comment_10508 Can you please advise me of the following. Your website states that "Fire doors will have automatic closing devices (fire door closers) fitted. " but is this talking about compartmentation doors like flat entrance doors or does it include bedroom doors to flats, as Building Control state that perecos are not required on bedroom doors, even ones that open onto a 30min protected hallway withing the flat. Can you help clarify please. Dave Report
July 15, 20178 yr comment_10517 Flat front doors still require closers. Flat internal doors used to require closers, but this was dropped in revisions to Building Regulations as they were almost universally removed by residents. You don't need to fit them and if you have an older flat you no longer need to retain them. Report
July 16, 20178 yr comment_10519 The guidance document 'Fire Safety in Purpose Built Blocks of Flats' by the Local Government Association covers this subject. Report