Guest Jay Taylor Posted February 14, 2017 Report Share Posted February 14, 2017 Do you have to have a separate fire alarm zone for the attic/loft area to the floors below? I know Zones should not cross floors but is the attic/loft classed as a separate floor? Quote Link to comment Share on other sites More sharing options...
AnthonyB Posted February 14, 2017 Report Share Posted February 14, 2017 BS 5839-1:2013 13.2 Recommendations 13.2.1 Recommendations applicable to all detection zones b) If the total floor area of the building is greater than 300 m2, each zone should be restricted to a single storey. d) For voids above or below the floor area of a room, these may be included within the same zone of the room, provided that the voids and the room constitute a single fire compartment. Depends whether you class it as a void or a floor. If the space is used and has an access ladder/stair I would be leaning towards calling it a floor, if a disused space more likely a void, but in the case of the latter would want remote indicators fitted. Quote Link to comment Share on other sites More sharing options...
Guest Jay Taylor Posted February 15, 2017 Report Share Posted February 15, 2017 Thanks AnthonyB Quote Link to comment Share on other sites More sharing options...