Do fire doors need latches?

Featured Replies

Hi,
Information seems varied on the topic of fire doors. Basically, looking for clarification that it is OK to not have latches if there is an overhead door closer present on a fire door. Many Thanks

Hi Donna,

Yes you are right. Info on fire doors is very varied and this is because the scope of what you can do (and can't do) depends on the fire test evidence for that particular door. So in answer to your question you can have a fire door 'unlatched' and held closed by the self closing device provided that the door has test evidence for that use. Check with the door supplier / manufacturer, if its a new one they should be able to supply certification and product data sheets with the info you need. Any more fire door related questions.........please don't hesitate.

Regards,

Neil Ashdown

Fire Door Inspection Scheme

Most fire door assemblies fitted with single axis hinges (butt hinges) and fitted with mortise latches rely upon the latch bolt to make an important contribution to the performance of the door in the event of fire, the self-closer alone would not be sufficient. The latch prevents the fire door from distorting in the initial stages of the fire. If you require a fire door without a latch then you would need a pivot hinge and the test details that come with the door should indicate this is possibility.

  • 5 months later...

Hi,

re fire doors not needing a latch if a fire-rated self closer is fitted, how can I determine which is a suitable fire-rated closer in this situation? Which fire door closer types are suitable. Are they marked as such, i.e. suitable for use without door latches?

Regards,

Scott

The only self closer I have seen that doesn't use a latch is a pivot hinge (floor hinge) which I have seen used on double doors in a corridor. As far as I am aware there is no marking which denotes this and I would imagine you would need to contact the manufacturer to check this out.

  • 3 years later...

all fire doors at Banatines health spa have NO latches

are they breaking the law???

Do they have other means of securing the door closed to prevent it opening without requiring a positive action to open it. 

Unlatched fire doors are common place especially in corridor situations where a latch would be an unnecessary hindrance. Check with the door manufacturers' installation instructions / data sheet that the door has suitable evidence of fire performance 'unlatched'.  Similarly, make sure the self-closing device has evidence of fire performance for use with an unlatched fire door.  The usual fire rated BS EN 1935 good quality butt hinges are suitable for unlatched fire doors.

Section 3 of 'The Code of Practice: Fire & Escape Doors' at http://firecode.org.uk/Code of Practice 2009 Issue 3.pdf provides further information.

An example of the documentation you should receive when you purchase a certified fire door, http://www.premdor.co.uk/pdf/download-centre/fire-certificates/certifire-cf-195-certificate-of-approval.pdf. If it is not a certified fire door then you could use the services of a fire door inspector.

  • 4 weeks later...

Hi. Quick question I hung some fire doors today and my customer is not happy because  there is no fire sticky tape around the latch when it’s in the door, is this a legal requirement or not ? 

I do not know what fire sticky tape around the latch when it’s in the door means, what is fire sticky tape?

Matty,  Are you referring to intumescent gasket material?   This material is fitted around the lock-case / latch-case and behind the forend and keep.  It is commonly required for use with timber based FD60 doors but not always for FD30 doors depending on the door's test evidence and the lock case size.

You should consult the door's data sheet with regard to permitted latch/lock and any requirement for intumescent gaskets.

Join the conversation

You are posting as a guest. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.