Linear gap sealing when dot and dab plasterboard in use on a blockwork wall

Featured Replies

In BS 8214 2016 none of the diagrams show dot and dab plasterboard as to where the sealing should be - i.e should capping seals be covering the gap in blockwork upto a door lining and brought to the face of the plasterboard closing off the void to the rear of the pasterboard as well? Or if joints to a lining and blockwork are tight, should that joint be opened up to min 5mm to place a capping seal here? 

If the joint between the timber door frame and blockwork wall is so intimate that there's no gap, then there is no linear gap to be sealed. Where there is such a gap it should be sealed using BS 8214 guidance. Intumescent sealant should be present level with the edge of the door frame and face of the wall.

Join the conversation

You are posting as a guest. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.