Guest Stu Posted June 26 Report Posted June 26 Looking to find a solution of where to rout and install cold and smoke seals on this rebated server room fire door if anyone could suggest? Thanks Quote
Neil ashdown Posted Monday at 10:46 Report Posted Monday at 10:46 Please send image of door in the closed position from inside the server room. Looking for somewhere suitable to locate a smoke seal as unsure there's room for a compression/batwing seal within the existing rebate? Quote
Guest Stu Posted Tuesday at 08:26 Report Posted Tuesday at 08:26 Hi Neil and thanks for your reply. Please see the internal photo of the door. Quote
Neil ashdown Posted 18 hours ago Report Posted 18 hours ago No options for smoke seals on the pull-side so check the rebates to see if the batwing will fit. When these are fitted the door must self-close completely and reliably. There may already be intumescent seals integral to the door leaf behind lipping at the vertical and top edges? Check this before making a groove in the door. If you are fitting intumescent seals though, the smoke seal could be incorporated into those. Quote