Guest Stu
Posted

Looking to find a solution of where to rout and install cold and smoke seals on this rebated server room fire door if anyone could suggest?

Thanks

Rebated Door 3.jpg

Rebated Door.jpg

Rebated Door 2.jpg

Posted

Please send image of door in the closed position from inside the server room. Looking for somewhere suitable to locate a smoke seal as unsure there's room for a compression/batwing seal within the existing rebate?

Posted

No options for smoke seals on the pull-side so check the rebates to see if the batwing will fit. When these are fitted the door must self-close completely and reliably.

image.png.2750c6fd15943d2b6807aecdaa72dd1c.png

There may already be intumescent seals integral to the door leaf behind lipping at the vertical and top edges? Check this before making a groove in the door. If you are fitting intumescent seals though, the smoke seal could be incorporated into those.

image.png.8486c1213bf272a75767be4e9a338de5.png