Guest Tom Posted April 24 Report Posted April 24 Hi we have had a FD60 installed in a softwood frame. The frame also has a side panel. The drawing states the door should be an FD30S. If the door is rated higher is this an issue? Also the fire seals cut on the frame are not central it looks like someone has cut them to upgrade to be fire rated. Would a new door set be required? Quote
Neil ashdown Posted Monday at 16:41 Report Posted Monday at 16:41 If you require an FD30 door there's no problem using a 54mm thick (potentialy FD60) door leaf. If single leaf door, the seals should usually be central. Can't say more without seeing the door in the flesh. Quote