Guest Perry Pattison Posted July 14 Report Share Posted July 14 Fire door installed 2011 comes with full paperwork stating FD 30/60 and has upvc frame fully steel reinforced and intumescent strips. Does this still comply with latest regulations.?. Quote Link to comment Share on other sites More sharing options...
AnthonyB Posted July 15 Report Share Posted July 15 AS long as the paperwork says a uPVC frame is actually acceptable and it was installed in accordance with the manufacturer's instructions using their approved compatible components and is still in undamaged working order then yes. Depending on location it may have been meant to have been installed with smoke seals and also it's either a 30 minute door or a 60 minute door it can't be both. Quote Link to comment Share on other sites More sharing options...