Paul B Posted June 20, 2023 Report Share Posted June 20, 2023 Hi All Is it necessary to have AFD in a lift shaft where the motor and associated components are enclosed in the lift shaft and not in a separate location? Should there also be AFD on each floor within a certain distance of the lift entrance? This is a three storey multi occupied office building with the lift located in a protected storey exit. Many thanks for your advice. Quote Link to comment Share on other sites More sharing options...
AnthonyB Posted June 21, 2023 Report Share Posted June 21, 2023 What category is the system intended to meet? Quote Link to comment Share on other sites More sharing options...
Paul B Posted June 22, 2023 Author Report Share Posted June 22, 2023 Hi Anthony it’s an L2 system. Quote Link to comment Share on other sites More sharing options...
AnthonyB Posted June 26, 2023 Report Share Posted June 26, 2023 In which case yes to both as per paragraph 22.2(c) of BS5839-1:2017 Quote Link to comment Share on other sites More sharing options...
Paul B Posted June 28, 2023 Author Report Share Posted June 28, 2023 That's great, thanks Anthony. Quote Link to comment Share on other sites More sharing options...