Building regulations for block of apartments


Ronan

Recommended Posts

It's quite clear in Table B1 to the 2020 edition of the Technical Guidance Document B to the Building Regulations 2006, the doors is required to be to Classification E30 Sa as defined in I.S. EN 1634-3: 2004 as restricted smoke leakage at ambient temperatures is needed. (In the UK this would be known as a FD30S door)