Guest Clare Smart Posted November 16, 2022 Report Share Posted November 16, 2022 Can anyone help me. I've been asked by a client if they could avoid the expense of providing 60 minute fire rated boarding between their commercial units and the flats above, if the commercial units became empty? I can't find any particular guidance around this and wonder if it just comes down to a risk assessment? Any help would be appreciated. Many thanks. Quote Link to comment Share on other sites More sharing options...
AnthonyB Posted November 21, 2022 Report Share Posted November 21, 2022 It would be down to risk assessment - empty does not mean risk free (which is why vacant premises are not exempt from the Fire Safety Order). I'd be looking at things including: Removal of all combustible materials and waste Isolation of gas & electricity security against arson & unlawful occupancy as part of determining if it was tolerable or not Quote Link to comment Share on other sites More sharing options...