Jump to content

Fire Alarm Activation - Voice Messages & Intermittent Sounders


MFD

Recommended Posts

Hi All,

Does anyone know what the minimum/ maximum recommended time delay is between hearing the audible fire alarm activation voice messages and the intermittent sounders that follow that message.

This is for an 8 story open planned  cooperate office building.

Many thanks 

MFD

Link to comment
Share on other sites

It should be the other way around on a loop. Voice alarm systems should generally operate in the following repeating sequence (BS5839-8):

  1. Attention-drawing signal – lasting 2 s to 10 s followed by
  2. Brief silence – lasting 1 s to 2 s followed by
  3. Evacuate message followed by
  4. Silence – lasting 2 s to 5 s
Link to comment
Share on other sites

Join the conversation

You are posting as a guest. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

Loading...
×
×
  • Create New...