Tonyc8310 Posted July 7, 2022 Report Share Posted July 7, 2022 Can anyone point to requirement to have a blue mandatory warning sign on residents bedroom doors in care homes that have a swing free device fitted? Is there an exemption on bedroom doors being required to have these under building regulations? Thank You Quote Link to comment Share on other sites More sharing options...
Mike North Posted July 11, 2022 Report Share Posted July 11, 2022 Approved Document B 2007 Appendix B Paragraph 9 The following fire doors are not required to comply with paragraph 8 a. Doors to and within flats b. Bedroom doors in other residential premises c. Lift entrance/landing doors Quote Link to comment Share on other sites More sharing options...