May 4, 201214 yr comment_2055 Hi In warehouses what distance should stock be stored from sprinkler head? Thanks Andy Report
May 4, 201214 yr comment_2060 I have never been involved closely with installation of sprinklers but the British Standard is BS EN 12845:2004+A2:2009 Fixed firefighting systems. Automatic sprinkler systems. Design, installation and maintenance. For Further information go to http://www.firesafe.org.uk/industrial-fire-sprinklers/ Report
May 5, 201214 yr comment_2062 Andy check out http://fire.org.uk/forum/index.php?topic=5779.new#new and you will see it becomes quite complicated. Report
June 14, 201213 yr comment_2230 According to NFPA 13, the sprinkler distance from top of storage to the sprinkler heads for traditional heads is 405 mm. For ESFR heads, it is 0.9m Regards Pierre Report
June 16, 201213 yr comment_2242 Be careful NFPA 13 is an American Code and there can be a variance between there codes and European standards. Report