  1. In a six storey block of balcony access flats there is a stairwell at one end providing access to the upper floor levels.  There is a secondary means of escape from the flats along the balconies to a stairwell at the opposite end of the block.

    However, before reaching the lobby door to the secondary stairwell, the balcony becomes a short corridor.  There is a flat and some service cupboards that open onto the corridor next to the lobby door to the stairwell.  So this corridor is effectively an extension of the balcony but is enclosed on all sides except being open to the atmosphere at one end.

    As there is two directional escape from the flats located along the 'fully' open balcony, then fire rated construction is not required in that location.  However, does this section of corridor need to be fire rated? (i.e. including the flat and service cupboard doors).

    I have come across many similar scenarios along these lines where flat entrance doors are located within partially-enclosed corridors/lobbies off open stairwells/access balconies. However, I have not come across any guidance indicating where fire rated construction is required/recommended (or not).    

  2. 21 hours ago, AnthonyB said:

    Q1. Even if every flat has it's own entrance if deemed part of the same building then in theory based on how you read it yes, the FSA would apply - however as this would potentially pull in semi detached houses I think the guidance that is to be released may well clarify that it only applies to buildings with internal common parts as well.

    Q2. Yes

    Thanks Anthony. Q1 - The revised FSO applies "Where a building contains two or more sets of domestic premises".  I would consider that a 3 storey period terraced house converted into 2 flats (both with their own external entrances - one at lower ground, one at upper ground level) would be included in this definition.  However, I would not consider a traditional pair of semi-detached houses as one building in the same sense.

    It will be interesting to see what the guidance says about this.

  3. On 25/06/2021 at 11:43, Tom Sutton said:

    A block of flats must have staircase's therefore must have common areas and it will depend on the fire strategy for the building and the type of fire alarm required or not according to the fire risk assessment. 

    Thanks Tom.  However, the typical blocks of flats that come into this category are 2 or 3 storey houses converted into 2 flats, both with external entrances (often one at lower ground floor level, the other upper ground floor level).  So there are no communal staircases. 

  4. Does the new Fire Safety Act 2021 now require a fire risk assessment to be carried out of blocks of flats with no common areas? (i.e. the external walls, doors, windows and balconies need to be assessed).

    Also, where a block of flats of this type is converted from a house (e.g. Victorian/Georgian terrace) not in accordance with modern Building Regulations, should there be a linked fire alarm system between the flats?   

  5. The ground floor storey of a modern purpose built block of flats is separate from the upper storeys.  There is an external communal entrance door that leads to a corridor, at the end of which there is a door which leads to a flat lobby with entrance doors to three flats.  There is a riser cupboard (with landlord's consumer unit and water pipes) within the entrance corridor and access panels to service duct/risers within the flat lobby.  The flats do not have alternative external exits.

    Is there any guidance that applies to this scenario in relation to means of escape, travel distances, ventilation requirements etc? (for example, is it a case of adapting the guidance for "Flats served by a single escape stairway" in the Purpose-Built Blocks of Flats guide to apply where 'outside' is effectively the stairway?)

  6. When applying the LACoRS guidance to houses converted to self-contained flats (prior to 1991) is the extent of the shared internal communal area irrelevant when counting the number of storeys (section 37)?

    For example, a three storey property has only a small communal lobby at ground floor level only with two flat entrance doors located within this lobby. Flat A occupies the ground floor only. Flat B occupies the upper two floors and the stairs are entirely within this flat (technically flat B is over three floors as its entrance is at ground floor level).

    As this is a three storey property, then Case Study D11 applies and a Grade A LD2 system (with control panel and call point) is recommended in the (small) common area linked to heat alarms in the entrance/lobby of each flat.

    Have I interpreted the guidance this correctly?

    Further, if there is a basement/lower ground floor flat in the block (flat C) that has its own separate external entrance and has no access to the communal area, does this flat also require a heat alarm linked to the communal system?

×
×