T.Pedersen Posted September 21, 2020 Report Share Posted September 21, 2020 Hi, I vaguely remember seeing a recommendation that the 5kg variant instead of the 2kg C02 should be installed where there is 400V+ present; is this correct as I can not find reference to this now? Thanks Quote Link to comment Share on other sites More sharing options...
AnthonyB Posted September 22, 2020 Report Share Posted September 22, 2020 No, it's an urban myth. The only reason why you might go for a 5kg for an electrical risk is if the size of the enclosure is such you need the larger volume of gas to flood it adequately. Quote Link to comment Share on other sites More sharing options...
T.Pedersen Posted September 22, 2020 Author Report Share Posted September 22, 2020 many thanks for clarifying Quote Link to comment Share on other sites More sharing options...
Recommended Posts
Join the conversation
You are posting as a guest. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.