Jump to content

Heat Detector Spacing


Mark1963

Recommended Posts

A query which has me puzzled on heat detector spacing.

BS5839 gives spacing of 5.3m from any point for detectors on horizontal ceilings.

However, it seems accepted that, within rooms, this should be halved to ensure overlap.  Many manufacturers technical guides show this.

I cannot see anything within the BS on this, and cannot see any circumstances where the 5.3m from any wall cannot be met .

Any ideas?

Link to comment
Share on other sites

Tom,
Thanks for this.  This is one of the better interpretations I have seen;

Where there is a requirement for more than one device in an area, these radii must overlap to ensure that there are no blind spots.

I have seen some sites that say the distance between detectors should be half of that stated in the BS to give the overlapping.

Link to comment
Share on other sites

Join the conversation

You are posting as a guest. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

Loading...
×
×
  • Create New...