Guest Sarah Posted July 23, 2019 Report Share Posted July 23, 2019 We have just had the emergency lighting at our premises tested in house (small system). Most of the lights were fine, but a couple were not at full brightness at the end of 3 hours. So the lights were functioning, but only at say 25% capacity after the full 3 hours. Is this acceptable, as they were still lit, do they all need to still be at full brightness? Quote Link to comment Share on other sites More sharing options...
AnthonyB Posted July 23, 2019 Report Share Posted July 23, 2019 They need to meet the minimum lighting level for the area - e.g. 1 lux on escape routes, 0.5 lux for open areas, etc. Quote Link to comment Share on other sites More sharing options...