February 20, 20197 yr comment_13584 Hello, heres a conundrum, how do you achieve fire detection on a building site that is part of a live site. Organisation is having the builders in to totally refurb the kitchen areas, place is being gutted BUT all around the other parts/outside the refurb area of the building are still occupied. Fire detection in the building part is being disconnected because ceilings are coming down, what if a fire occurs outside of hours when the builders are not there but the occupiers are in their part? Report
February 21, 20197 yr comment_13588 It all depends on the type of fire alarm installed, if it is only a type M system then I do not see many problems, if it is a type P system, then that is up to the owners or insurance to provide alternative protection, if it is a type L system then you would need to know the full layout of the fire alarm to give a definitive answer. Report