November 8, 20187 yr comment_12933 Do service risers need to be fire stopped at each floor level in a purpose built block of flats that operate a stay put policy? Report
November 9, 20187 yr comment_12941 If constructed as a protected shaft there isn't an automatic requirement, it's usually seen where a protected shaft approach isn't used or sometimes in fire strategies to give added protection where compartment floors are required. Report