June 1, 201313 yr comment_5545 Hi, when opening a New Nursery does it need to be fitted with a Fire Alarm ? Or can it be fitted with interconnected smoke detectors ? Thanks Report
June 1, 201313 yr comment_5546 I would suggest that you have a fire risk assessment carried out. I would also suggest that interconnected smoke alarms do not constitute a fire alarm. To expand on the above: Interconnected smoke alarms are acceptable for a domestic dwelling, but for use as a "Fire Alarm" they fail on several reasons. If a fire is discovered there is no way of manually initiating the alarm. (A fire alarm has manual call points) There is no sound volume requirement. (A fire alarm has to have a minimum sound level in all areas) They can be wired in non fire proof cable. (A fire alarm has to be wired in fire proof cable) The list does go on. Report
Join the conversation
You are posting as a guest. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.