January 7Jan 7 comment_55412 A two-foot square timber fronted riser cupboard on a stairwell of a 5-storey residential block of flats contains three waste pipes and three electric supply cables running up through all floors. The hinges are not fire-rated, the door is 18mm thick with 10mm stops. No combined seals. Is there a need to better protect the escape route? Report
January 12Jan 12 comment_55465 No distribution boards, meters or other equipment, just cables? Report
January 19Jan 19 comment_55554 Strictly speaking yes, but if at no point in the riser there are no meters, DNO fuses or distribution boards or anything liable to be an ignition source then you could make a case for tolerating it. Is it an open shaft or just with holes punched through floorboards or pipes & cables? Report
January 27Jan 27 Author comment_55657 On 19/01/2026 at 20:14, AnthonyB said: Strictly speaking yes, but if at no point in the riser there are no meters, DNO fuses or distribution boards or anything liable to be an ignition source then you could make a case for tolerating it. Is it an open shaft or just with holes punched through floorboards or pipes & cables? No meters, fuses or distribution boards, just three electric cables tunning up through punched holes up five levels. Waste pipes also within the block cavities. Guessing nothing is combustible and toleration is acceptable. Thanks Report
January 28Jan 28 comment_55681 I'd not consider it a major issue then, just seal any penetrations into the roof space and into surrounding areas that are not the stair core. Report
February 3Feb 3 Author comment_55717 On 28/01/2026 at 20:57, AnthonyB said: I'd not consider it a major issue then, just seal any penetrations into the roof space and into surrounding areas that are not the stair core. Ta muchly Report
Join the conversation
You are posting as a guest. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.