jagjeevan sansoa Posted February 7 Report Posted February 7 Hi Mr Sutton seeking you advice We have plant room doors to block of flats recently damaged due to an incident-- theses quite old and need replacing do we need accredited installer ? do vents need to fitted to doors as legal requirement kind regard Jag Sansoa Quote
AnthonyB Posted February 15 Report Posted February 15 You should ideally use an accredited installer to ensure that a certified doorset is correctly specified and installed (although admittedly it's no guarantee). Vents should be avoided unless the room includes plant requiring a minimum specification of ventilation (e.g. boilers) & there is no alternative such as external wall vents. If a fire door (e.g. FD30) they should be intumescent vents or if a firedoor also requiring smoke control (e.g. FD30s) then you would need the vent to be protected by an automatic fire and smoke damper linked to the fire alarm system, usually with detection either side. Quote