November 13, 20241 yr comment_45657 Can someone please confirm which fire system we need? The FRA said D LD2, but the building is four storeys high, including the basement, which houses three flats off the communal hallway. Report
February 3, 20251 yr comment_47022 If you're going by BS 5839-6:2019 for domestic properties then is depends on how the property is used and whether its a new build or existing. Report
February 3, 20251 yr comment_47060 On 13/11/2024 at 17:22, Guest matjwheeler@icloud.com said: Can someone please confirm which fire system we need? The FRA said D LD2, but the building is four storeys high, including the basement, which houses three flats off the communal hallway. If it's more than two stories then all relevant guidance requires a Grade A or Part 1 communal system with flat self contained systems being Grade D LD3 minimum, ideally LD2. This is assuming it's a converted premises requiring a simultaneous evacuation policy. If it's stay put you don't need the common system Report