Guest Peter Posted January 19 Report Share Posted January 19 We have just been told to install a FD30S fire door that was already on site. I asked to see the compartmentation drawings and it shows that the door should in fact be a FD60S. The client just wants us to fit it but I’m not going to. Is there any information I can get to show the client that’s not the right thing to do. I have looked at approved document B but can’t find anything that highlights this. Quote Link to comment Share on other sites More sharing options...
Mike North Posted January 22 Report Share Posted January 22 You need BR Appendix C, table C1 page 153 Quote Link to comment Share on other sites More sharing options...
Neil Ashdown MAFDI Posted January 22 Report Share Posted January 22 https://www.gov.uk/government/publications/fire-safety-approved-document-b Quote Link to comment Share on other sites More sharing options...