June 20, 20232 yr comment_37041 Hi All Is it necessary to have AFD in a lift shaft where the motor and associated components are enclosed in the lift shaft and not in a separate location? Should there also be AFD on each floor within a certain distance of the lift entrance? This is a three storey multi occupied office building with the lift located in a protected storey exit. Many thanks for your advice. Report
June 26, 20232 yr comment_37113 In which case yes to both as per paragraph 22.2(c) of BS5839-1:2017 Report