What fire/smoke alarms required in Hairdressing and Beauty Salon over 3 floors


Guest Vineet

Recommended Posts

Guest Vineet

Hello

We are opening a Hairdressing and a Beauty Salon over 3 floors

Hairdressing on ground floor and Beauty Services on 1st and 2nd Floor.

I need to know what kind of Fire / Smoke alarm will be required to meet British Standards.

There is escape window in every room of 1st and 2nd Floor.

There is also Fire Exit sign on every floor and non-maintained emergency light on landing / hallway of every floor.

 

Link to comment
Share on other sites

You are required by law to carry out a fire risk assessment which will determine your fire warning system requirements.

Due to the size of the premises it would require an electrical fire alarm system to BS5839-1 comprising manual call points at each exit from the premises and each landing, alarm sounders and a control panel. The risk assessment would determine if smoke & heat detectors were required as part of the system - usually this would be to escape routes.
https://www.safelincs.co.uk/fire-alarm-panels-and-fire-alarm-systems/

Domestic smoke alarms would not suit.

Link to comment
Share on other sites

Join the conversation

You are posting as a guest. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

Loading...
×
×
  • Create New...