Jump to content

fire protection of service riser


Guest ScottSaun

Recommended Posts

Guest ScottSaun

Hi Tom

Just a quick question with hopefully a simple answer...block of purpose built flats with a service riser going through each bathroom. The soil pipe from the WC in each bathroom goes into the riser. An access panel to the riser is required in each bathroom. What level of fire resistance does the access panel require, i.e. FD30, FD60, FD30S, FD60S? Looked at Approved Doc B but it's confusing!

Scott

Link to comment
Share on other sites

Join the conversation

You are posting as a guest. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

Loading...
×
×
  • Create New...