Guest Barry D Posted January 22, 2023 Report Share Posted January 22, 2023 Hi Has EVERY flat entrance door got to be a fire door, or if the flat front door opens to fresh air can it just be a normal door thanks Quote Link to comment Share on other sites More sharing options...
Mike North Posted January 23, 2023 Report Share Posted January 23, 2023 As a general rule flat entrance doors should be fire rated. The basic exception are when there is no door or window above them (top floor) and a person can get 1.8m away from the building without passing another door (a balcony for instance) Quote Link to comment Share on other sites More sharing options...