February 14, 20233 yr comment_34244 Hi has anyone seen this hold open device before. There is no information on it. It has been installed on a nominal FD30 door. Is it allowed if it’s only surface fitted? Report
February 17, 20233 yr comment_34429 On 14/02/2023 at 16:25, Guest Joe said: Hi has anyone seen this hold open device before. There is no information on it. It has been installed on a nominal FD30 door. Is it allowed if it’s only surface fitted? Looks like a hold open device used on the likes of a garage door. No it should not be used on a fire door, as it's not linked to your active alarm system, it's manually operated. Regards George Drayton Report
February 18, 20233 yr comment_34458 Not allowed because it fails to automatically release when the fire/smoke alarm is activated. Report