  1. Ok let's reset, as it sounds that the system has lost its information:

    1) set units to factory mode: press housecode button with screwdriver for 7 seconds til amber light has come on fully. Repeat with other unit

    2) test communication by pressing test button til sounder in both units is starting. Wait 2 minutes. Then repeat with second unit.

    3) Set housecode again: Press Housecode button with screwdriver for 1 to 2 seconds til amber light flashes with double flash every 5 seconds. Repeat with other unit. This type of flashing carries on for about 15 minutes.

  2. The fire alarm panel should be inspected visually on a daily basis for normal operation of the system and any defects should be recorded in a logbook and reported to a responsible person.

    A full system test should be carried out weekly including an examination of batteries and connections including electrolyte level, the test and any defects should be recorded in a logbook and reported to a responsible person.

    We do not sell fire alarm log books but we do have a free fire safety log book which contains a fire alarm testing section which can be downloaded below.

    I hope this helps you.

    Download our Free Fire Safety Log Book

  3. Silencing the alarms in case of a false alarm: In case one of the units detects smoke, all alarms sound. To silence the alarms in case of a false alarm, press the hush button on the unit that has detected the smoke. This will silence all alarms. If you do not know which detector caused the alarm, you can silence each alarm individually by walking from alarm to alarm and pressing the hush button. This will silence the individual alarm but the other alarms will continue to sound. This prevents a person silencing the system in case of a real fire.

×
×