BS 8214: 2016 Timber fire door assemblies: Code of practice states that, for doors that must restrict the spread of cold smoke, the threshold gap should be no greater than 3mm at any point. 

A 12mm gap is likely to be too large even for a fire door without the restricted spread of cold smoke requirement.  You will likely need to install a threshold plate to the floor in remediation. 

Link to post
Share on other sites

Hi,I'm supervising on a 20 story apartment block built 10 years ago.  Reducing the gaps head and sides 3mm + or - 1mm so 4mm max.

There are 450 communal doors to have remedial work done to them,  we are reducing the gaps, changing all hinges, changing the intumisent smoke seals, batt and mastic between frame and structure.  The threshold gaps are very bad, we have been told that the maximum permitted threshold gap is to be 10mm. The average gaps is 15mm with the worst 27mm.

I have been told that the manufacturer s certificate will not allow hardwood edging strips to be glued and screwed to the bottom of the door.  I suggest an 8mm metal threshold strip screwed to the carpets.  Was told this would cause a trip hazard. 

What would be the correct solution

Link to post
Share on other sites

Join the conversation

You are posting as a guest. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

Loading...
×
×
  • Create New...