Brad Parker

Borrowed Lighting

Recommended Posts

Questions reference borrowed lighting; 1) if the 'street lighting' is on the same phase as the 'premise lighting' and there is a power failure to the street lighting and/or area, then the premise has no emergency escape lighting.  Is this acceptable when considering designing emergency lighting systems 2) there are different lux levels, required at the points of emphasis within a premise i.e. centre line of an escape route and say, a manual call point.  How is the photometric data gathered and designed around borrowed lighting, when most certainly shadows will form in areas not covered by windows.

Thanks.

Share this post


Link to post
Share on other sites

Your points are valid and why every revision of BS5266 reduces the acceptance of borrowed lighting more  & more and if you have an escape route and open area that at any time of use would require you to switch the electrical lighting on there is a good chance you will need emergency lighting.

Share this post


Link to post
Share on other sites

1.  Brad today it’s all about risk assessment so what are the chances of a fire on the premises, the electric supply and external lighting failing at the same time, I would think pretty low consequently an acceptable risk.

2.  If you are accepting borrowed light as acceptable, then you do not require emergency escape lighting therefore photometric data is not necessary.  I would conduct an inspection during the hours of darkness, switch off the lights, if I can find my way about and see what I need see, then emergency lighting is not needed. I accept it cannot be done off plan.

Share this post


Link to post
Share on other sites
Guest ADVANCE FIRE YORK

To save any confusion, this is what is now stated in the most recent Emergency Lighting British Standards.

BS 5266-1:2016, Clause 3.1

“Borrowed light
light obtained from an adjacent reliable source that is expected to be available at all material times

NOTE For example, from a local emergency luminaire.”

 

 

Share this post


Link to post
Share on other sites

 Local emergency luminaire is only an example there would be others, street lighting and daylight for example, so nothing has really changed.

Share this post


Link to post
Share on other sites

Your content will need to be approved by a moderator

Guest
You are commenting as a guest. If you have an account, please sign in.
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

Loading...

×