If a site has a means of raising an alarm (call points) but no detection, do they have to carry out any servicing other than weekly tests?

I understand an detection system with a fire panel should be serviced and maintained at least twice per annum but I'm not sure if there is no panel and no detection.

Thanks

Jon

Share this post


Link to post
Share on other sites

A fire alarm has four areas, the detecting circuit, the sounding circuit, the control and indicating equipment, and a back up battery. Your detecting circuit is the manual control points making it a M category system and if you do not have the other items then it will not conform to BS 5839 part 1. In all situations it should conform to BS 5839 which requires the six monthly tests.

Share this post


Link to post
Share on other sites

If you have no control panel and just call points, bells/klaxxons and a mains switch at the distribution board then you have a VERY old 3 wire 240V fire alarm system that not only does not conform to British Standards (& didn't 35 years ago either) but contravenes the Health & Safety (Safety Signs & Signals) Regulations 1996 as it does not have a secondary power supply.

It cannot be serviced to BS5839-1 and due to the simplicity only requires rotational weekly testing of call points, as the only thing a service engineer could do is a mega weekly test just using a lot more call points.

The system will require replacement.

Share this post


Link to post
Share on other sites
Guest Call points

Hi , I’ve been asked to add a call point to a smoke alarm system which has no control panel . Is this possible or do I need To  recommend installing one ? 
thanks Paul 

Share this post


Link to post
Share on other sites

The premises should have call points first before detection - domestic smoke alarms are normally not suitable for commercial premises (unless of course you are talking about a HMO where in smaller ones they are OK)

Not all Grade D smoke alarm systems can have call points added so knowing what exactly you've got would help.

A proper fire detection & warning system to BS5839-1:2017 may be required if it's a commercial building.

Share this post


Link to post
Share on other sites

Join the conversation

You are posting as a guest. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

Loading...

×
×
  • Create New...