I am just setting up as a mobile disco and am concerened about using smoke machines and setting off smoke alarms. Is there any way I can use my smoke machine depending on what type of alarms are fitted or will the smoke trigger all alarms?
Many would just say, don't use the smoke machine but it gives a venue atmosphere and customers are not very happy if I have not been able to provide them with what they would class as an atmospheric disco event.
Smoke alarms and disco smoke machines
Started by
Guest_DiscoKid_*
, Feb 03 2012 02:42 PM
12 replies to this topic
#2
Posted 07 February 2012 - 09:10 AM
Check out http://www.nodj.co.u...e-machine.shtml Safety and usage information which says,
The smoke can activate smoke detectors and this is something that you should check with the venue first. Many venues have more advanced smoke detectors that allow this type of smoke, but some don't and the venue staff will be able to tell you if it's OK to use a smoke machine.
Which is pretty good advice, it all depends on which type of smoke detectors are being used, the type of smoke, the amount of smoke, the size of the room, and the potential temperature of the room. As I have said it all depends, even steam from a shower can activate a detector head if the conditions are right.
The smoke can activate smoke detectors and this is something that you should check with the venue first. Many venues have more advanced smoke detectors that allow this type of smoke, but some don't and the venue staff will be able to tell you if it's OK to use a smoke machine.
Which is pretty good advice, it all depends on which type of smoke detectors are being used, the type of smoke, the amount of smoke, the size of the room, and the potential temperature of the room. As I have said it all depends, even steam from a shower can activate a detector head if the conditions are right.
All my responses only apply to England and Wales and they are an overview of the subject, hopefully it will point you in the right direction and always treat with caution. Scotland and Northern Ireland has differing legislation
#4 Guest_Zak Nicholson_*
Posted 20 February 2012 - 09:20 PM
Hi,
I'm a Lighting and sound technician within a school, and we have our smoke detectors that get set off by using smoke machines/haze machines for shows, what we do is get our site team to turn off the detectors in that particular zone during a show (during the time that the detectors are off, there are members of staff always within this area to raise the alarm if a fire was to occur)
What the site team have told me is that the smoke dectors are degrading in life, due to turning them on and off, some how I don't believe this is true. Please can you confirm this for me?
I'm a Lighting and sound technician within a school, and we have our smoke detectors that get set off by using smoke machines/haze machines for shows, what we do is get our site team to turn off the detectors in that particular zone during a show (during the time that the detectors are off, there are members of staff always within this area to raise the alarm if a fire was to occur)
What the site team have told me is that the smoke dectors are degrading in life, due to turning them on and off, some how I don't believe this is true. Please can you confirm this for me?
#5
Posted 21 February 2012 - 10:59 AM
The sensors in a smoke alarm will degrade over time. This along with years of exposure to dust and contaminants will cause detector performance to falter. Thus smoke alarms should be replaced periodically in accordance with manufacturers’ recommendations. Whether isolating a zone will up speed this process up is debatable and I would suggest you contact the manufacturer for their recommendations.
As to isolating a zone this is not a good practice, you could be removing the protection of a concealed area. I would suggest you consider changing the affected detector heads with a more suitable head that is not sensitive to the smoke machines. Your fire alarm engineer should be able to assist you with this.
As to isolating a zone this is not a good practice, you could be removing the protection of a concealed area. I would suggest you consider changing the affected detector heads with a more suitable head that is not sensitive to the smoke machines. Your fire alarm engineer should be able to assist you with this.
All my responses only apply to England and Wales and they are an overview of the subject, hopefully it will point you in the right direction and always treat with caution. Scotland and Northern Ireland has differing legislation
#6
Posted 21 February 2012 - 11:24 AM
We are not aware that there are any detrimental effects from switching off smoke detector heads.
I would take particular care to ensure that the loops are re-activated after temporary switch-off. How about leaving your car keys near the fire alarm panel?
Harry
I would take particular care to ensure that the loops are re-activated after temporary switch-off. How about leaving your car keys near the fire alarm panel?
Harry
#8
Posted 30 March 2012 - 01:59 PM
In my opinion answer is no if a smoke detector has been installed as required by the fire risk assessment then replacing it with a heat detector will reduce the response time, to a fire alarm, putting lives in danger.
Have you considered bringing in a fire alarm specialist to look at the problem and maybe s/he could provide a solution.
Have you considered bringing in a fire alarm specialist to look at the problem and maybe s/he could provide a solution.
All my responses only apply to England and Wales and they are an overview of the subject, hopefully it will point you in the right direction and always treat with caution. Scotland and Northern Ireland has differing legislation
#10
Posted 16 April 2012 - 06:42 PM
Hi, I would agree with the fire officer. Fixed temperature heat detectors activate at around 90 degrees c. Some fire panels have a "fire delay" option perhaps yours has. The idea of it is that the panel indicates fire but the sounders are delayed for a short time so you can investigate the cause.
#11
Posted 17 April 2012 - 08:40 AM
I am trying to find an answer but it may take some time assuming one exists. I have come across a detector called Advanced Multi-Criteria Fire Detector and you could check it out and see if it solves the problem.
Check out http://www.esmagazin...s-system-sensor and www.systemsensor.com/pdf/COPTIR-performance-report.pdf another make by Honeywell http://www.notifier....adv-sensing.htm
Check out http://www.esmagazin...s-system-sensor and www.systemsensor.com/pdf/COPTIR-performance-report.pdf another make by Honeywell http://www.notifier....adv-sensing.htm
All my responses only apply to England and Wales and they are an overview of the subject, hopefully it will point you in the right direction and always treat with caution. Scotland and Northern Ireland has differing legislation
#12
Posted 18 April 2012 - 01:26 PM
Welcome green-foam its nice to have more support on the answers side.
All my responses only apply to England and Wales and they are an overview of the subject, hopefully it will point you in the right direction and always treat with caution. Scotland and Northern Ireland has differing legislation
#13
Posted 20 April 2012 - 10:18 AM
The Fire Alarm System has to be an addressable type system and,
I think the best solution would be replacing the offending heads with advanced multi-criteria fire detector heads (4 sensors) if the control panel is compatible and you are prepared to accept the higher cost/availability. (Like System Sensor or Honeywell Notifier IntelliQuad)
Another solution would be to program all the offending detector heads and program them to reduce their sensitivity, or build-in a simple key switch to the system that automatically isolates the required affected detection heads. At the same time, provide various visual and/or audible warning that the system is in a 'partially disabled' state.
The problem with smoke machine fog is that it is hard to control it at a level that will definitely not affect your 'adjusted less-sensitive' detectors. You end up still getting some, if as not as many, unwanted alarms. It is far more practical to temporarily totally isolate automatic detection in the smoke machine affected areas during those times those areas have people present.
A further safety requirement would be to conduct a fire risk assessment for when the smoke machine is in use and also produce a Permit to Work system covering the use of smoke machines, part of the sign off procedure is to reinstate the fire alarm system.
Any fire, in the area that involves the fog from the machine, would soon be discovery by the persons present or the staff dedicated to fire watching in this area.
I think the best solution would be replacing the offending heads with advanced multi-criteria fire detector heads (4 sensors) if the control panel is compatible and you are prepared to accept the higher cost/availability. (Like System Sensor or Honeywell Notifier IntelliQuad)
Another solution would be to program all the offending detector heads and program them to reduce their sensitivity, or build-in a simple key switch to the system that automatically isolates the required affected detection heads. At the same time, provide various visual and/or audible warning that the system is in a 'partially disabled' state.
The problem with smoke machine fog is that it is hard to control it at a level that will definitely not affect your 'adjusted less-sensitive' detectors. You end up still getting some, if as not as many, unwanted alarms. It is far more practical to temporarily totally isolate automatic detection in the smoke machine affected areas during those times those areas have people present.
A further safety requirement would be to conduct a fire risk assessment for when the smoke machine is in use and also produce a Permit to Work system covering the use of smoke machines, part of the sign off procedure is to reinstate the fire alarm system.
Any fire, in the area that involves the fog from the machine, would soon be discovery by the persons present or the staff dedicated to fire watching in this area.
All my responses only apply to England and Wales and they are an overview of the subject, hopefully it will point you in the right direction and always treat with caution. Scotland and Northern Ireland has differing legislation