Fire Door Seals in wrong position?


Recommended Posts

Good morning,

Would you be kind enough to give me some advice regarding the above withing a domestic property please?

We had a fire door & intumescent fire strip fitted in our property when we had an extension done recently.

The fire door was between our garage & our utility room as part of the new extension.

The strip has been fitted between the framework before the fire door on the utility side of the door (leading into our garage)

Several people withing the building trade & a Fireman have advised its incorrect & in wrong place?

Sounds like it should either be withing the actual door itself or withing the framework on the other side of the door (garage side)?

We're not 100% sure but obviously a bit concerned due to health & safety & also there being an isue with getting through the building inspector etc??

Would you be kind enough to confirm if this is in fact wrong, and whether I should seek an independent assessor of some description ie from the council etc to check & verify?

Link to comment
Share on other sites

Good morning,

Would you be kind enough to give me some advice regarding the above withing a domestic property please?

We had a fire door & intumescent fire strip fitted in our property when we had an extension done recently.

The fire door was between our garage & our utility room as part of the new extension.

The strip has been fitted between the framework before the fire door on the utility side of the door (leading into our garage)

Several people withing the building trade & a Fireman have advised its incorrect & in wrong place?

Sounds like it should either be withing the actual door itself or withing the framework on the other side of the door (garage side)?

We're not 100% sure but obviously a bit concerned due to health & safety & also there being an isue with getting through the building inspector etc??

Would you be kind enough to confirm if this is in fact wrong, and whether I should seek an independent assessor of some description ie from the council etc to check & verify?

The seals should either be on the 44mm wide side of the door or in/on the frame facing the side of the door. The seal should not be facing the large leaf of the door!

Link to comment
Share on other sites

  • 3 weeks later...

I agree with Torx if you go to http://www.firesafe.org.uk/fire-doors/ there is a diagram showing the location where the intumescent strip should be fitted. On both long sides and the head of the fire door. Try http://www.ifsa.org.uk/pdf/Information%20Sheet%20No1.pdf for more info.

Link to comment
Share on other sites

  • 3 years later...

Join the conversation

You are posting as a guest. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

Loading...
×
×
  • Create New...